This instruction manual is intended to help you understand the control system breathing apparatus SCAD-I for the purpose of its correct and safe operation. The manual describes the principle of operation, the design of the system, provides rules for preparing the system for operation and working with it, checking its technical condition, conditions for transportation and storage.

Information is presented from the OPERATION MANUAL SCAD 1.00.000RE

Available for download after the article.

1 Design and operation of the system

  • Purpose of the system
  • System completeness
  • Marking

2 Using the system as intended

  • Preparing the system for operation
  • Working with the system
  • Operating instructions
  • Maintenance
  • Security measures
  • Transportation and storage
  • Possible malfunctions and methods for eliminating them

Check No. 1 DASV PTS Profi M

DEVICE AND OPERATION OF THE SYSTEM

  • Purpose of the system.

The SKAD-1 breathing apparatus monitoring system (hereinafter referred to as the system) is designed to check the performance of breathing apparatus with compressed air type AIR-98MI, ​​PTS "Farvater", PTS "Spasatel", PTS

PSS 7000, Drager Man PSS 90, BD 96, BD Compact, Air MAXX, Air GO and front parts of PTS “Obzor”, PTS “Obzor”-S, PM-2000, MP-01, Panorama Nova Standard, f2, Pana Sil , 3S-PF, Ultra Elite-PF for compliance with the requirements set out in the operating manuals for breathing apparatus, “Manual on the gas and smoke protection service of the State Fire Service of the Ministry of Internal Affairs of Russia” and NPB 309-2002.

The system is intended for operation in stationary conditions at control posts and GDZS bases, as well as as part of the equipment of GDZS vehicles.

The system allows you to carry out the following types checks:

  • the value of vacuum air pressure at which the lung demand valve is turned on;
  • the amount of excess air pressure created by the lung demand valve;
  • the magnitude of excess pressure in the under-mask space of the front part at zero air flow;
  • the amount of air pressure at which the exhalation valve of the front part opens;
  • quantities reduced pressure, opening pressure of the safety valve and tightness of the gearbox valve;
  • tightness of the air duct system of the breathing apparatus;
  • tightness of the front part under vacuum pressure;
  • tightness of the rescue device at vacuum pressure;
  • the value of the vacuum air pressure at which the valve of the lung demand valve of the rescue device opens without excess pressure under the front part.

The system is made in climatic version Category 4 according to GOST 15150, but for operation at ambient temperatures from 5 to 50C and relative humidity up to 80%.

The system is available in two versions:

  • control and measuring unit with a head dummy;
  • control and measuring unit with test disc.

The head dummy is made in 2 versions: with a plastic fofan (MG version) and with a rubber compound fofan with a pressurization system (MGn version).

Example of system designation when ordering:

Breathing apparatus monitoring system SKAD-1 with MGn head dummy according to TU 4212-017-46840277-2001.

ATTENTION! The SCAD-1 system is delivered to the consumer fully adjusted and ready for use. The system DOES NOT REQUIRE any additional adjustments. In case of violation of the integrity of the sealing places, the manufacturer declines all warranty obligations.

Main parameters and characteristics

Table 1

Parameter name Meaning
1 Measuring range of excess and vacuum pressure, Pa minus 1250...
2 Measurement range of reduced pressure, MPa 0 … 2,0
3 Time measurement range, s 0 … 3600
4 Useful pump volume, dm3, not less 0,5
5 dimensions, mm, no more 450 x 260 x 220
MG head model 380 x 280 x 220
headform MGn* 420 x 250 x 200
test disk 370 x 140 x 300
6 Weight, kg, no more 7,0
control and measuring unit
MG head model 1,8
MGn headform 2,5
test disk 3,5
7 Service life, years 10

* when the dummy is filled with air to a pressure in the range of the green sector of the indicator scale.

  • Completeness of the system.

The completeness of the system is shown in the table

table 2

Continuation of table 2

1 2 3 4
orDummy head MGn or

Test disk DIP 88

PTS 76.00.00.000

DIP 88.00.000

1
2 Spare parts kit SKAD.20.000 1
3 Packaging, including: 3.1 Box

3.2 Container for the dummy

3.3 Box or Carton

U1.00.000 SKAD.52.000 U1.00.000 1 for headform

for test disc

4 Documentation, including: 4.1 Operating manual

4.2 Passport

4.3 Operating instructions for the MGn headform

4.4 Passport for pressure gauge

4.5 Passport for pressure and vacuum gauge

4.6 Passport for a stopwatch

4.7 Spare parts list

SKAD1.00.000RE SKAD1.00.000PS

PTS 76.00.00. 000RE

Type 111.12.050

Type 612.20.100 4282N/001000 SKAD1.00.000ZI

1 **

* – the MG head dummy is used to check imported facial parts, the test disk is used to check the front parts made on the basis of the PM-88 mask, all front parts are checked on the MGn head dummy.

** – when the system is supplied with a MGn head dummy

Composition, marking and purpose of adapter kit parts

Table 3

PTS “Profi” PTS “Spasatel” PTS “Farvater” Pulmonary demand valve hose SKAD.15.0022 Adapter for connecting the device connector to BRSAP-98-7K AP-2000

AP "Omega"

Connector SKAD.15.003 SKAD.15.0093 Adapter with external thread M45x3 and internal thread 40x4 and gasket

All types Pulmonary demand valve of rescue device (without overpressure)

Continuation of table 3

017 Plug of lung demand valve line. All typesHose

lung demand valve SKAD.15.0088 Plug of the exhalation valve of the front part type ShMP All types with ShMP Exhalation valve SKAD.15.01010 Adapter with external thread M45x3 and a socket for connecting a pulmonary valve with a plug connection PTS “Profi” PTS “Farvater” PTS “Spasatel” PTS “Basis” PTS “Avia”

RA-94 Plus Drager PSS 7000 Drager Man PSS 90 Lung machine SKAD.15.02020 Adapter for connecting the “Drager” gearbox to the “Basis” BRSPTS PTS “Avia” RA-90 Plus RA-94 Plus

Drager PSS 7000 Drager Man PSS 90 Reduced pressure socket SKAD.15.03030 Adapter for connecting the device connector to the Basis BRSPTS PTS Avia AIR-300SV

RA-94 Plus Drager PSS 7000 Drager Man PSS 90 BD 96, BD Compact Air MAXX, Air GOConnectorSKAD.15.04040Adapter with external thread M20x1 and fitting for connecting the device to BRS.AP-98-7K AP-2000

AP "Omega" Pulmonary demand valve hose SKAD.15.050

*50Adapter for connecting a connector (marked PTS) to adapter SKAD.15.030 (without marking PTS) PTS “Profi” PTS “Basis” PTS “Avia” PTS “Spasatel” Connector SKAD.15.060

*60Adapter for connecting a connector (without PTS marking) to adapter SKAD.15.030 (with PTS marking) PTS “Profi” PTS “Basis” PTS “Avia” PTS “Spasatel” Connector

* – available upon special order.

Design and principle of operation of the system

  • System design.

The system (Fig. 1) consists of a portable plastic shockproof case 1 with a lid 2, a carrying handle 3, a lid lock 4, an eyelet for a transport seal 5, a compartment for adapters 6 and a button - lock 7.

The headform (or test disk) is designed to mount the facepiece when performing breathing apparatus tests.

The MG head dummy consists of a body 8 with a fitting 9 and a tube 10, through which the under-mask space is connected to the system.

The check disk consists of a housing 11 mounted on a bracket 12. A front disk 14 and a connecting nipple 15 with a tube 16 are secured to the housing with a nut 13. The flywheel 17 and the pressure disk 18 mounted on it are moved along the threaded part of the housing using a handle 19.

The design and principle of operation of the MGn head dummy are given in the operating instructions for the dummy.

The control and measuring unit is located in the system housing. The unit controls, instrumentation and connection devices to the unit (coupling coupling and quick-release coupling) are located on the control panel.

On the control panel (Fig. 2) there is a connecting coupling 1 with a sealing gasket 2 and a plug 3, a button for releasing excess (or vacuum) pressure 4, an “excess-vacuum” switch lever 5, a pressure-vacuum gauge 6, a pump handle 7 with a lock 8, a button reduced pressure release 9, quick-release coupling (QCU) 10, reduced-pressure pressure gauge 11, stopwatch 12. A protective cap is put on the quick-release coupling.

  • Operating principle of the system.

The control and measuring unit of the system consists of two autonomous units (Fig. 3):

  • low pressure block;
  • reduced pressure block.

Low pressure block.

The source of pressure in the block is a manual piston pump 1 with a spring for returning the pump rod to the working (uppermost) position.

When you press the pump handle, air under pressure is supplied to pneumatic distributor 2, switching which to one of its positions determines the creation of excess or vacuum pressure in the block. From the pneumatic distributor, excess (vacuum) pressure flows to coupling 3, to which the unit being tested is connected directly or through an adapter, then to pressure-vacuum gauge 4, designed to control the pressure in the block, and pneumatic distributor 5, designed to relieve pressure in the block.

Reduced pressure block.

The reduced pressure from the air duct system of the breathing apparatus enters the unit through quick-release connection 6. The amount of reduced pressure is controlled by pressure gauge 7.

The pressure in the block is relieved by pneumatic distributor 8.

  • Marking.
  • The marking is on a plate attached to back wall housings.

The label states:

  • product code;
  • technical specifications number;
  • serial number of the product;
  • date of manufacture (month and year).

The headform is marked on a plate attached to the body of the headform.

The test disc is marked on a plate attached to the bracket.

The markings on the headform (or test disk) contain:

  • manufacturer's trademark;
  • name or code of the product;
  • product serial number;
  • date of manufacture (month and year).

USING THE SYSTEM AS INTENDED

Before using the system for its intended purpose, you must:

  • prepare the system for operation;
  • Check the tightness of the system with the headform (or test disk) connected.

Preparing the system for operation.

  • Install the system and head dummy (or test disk) at the workplace, open the housing cover.

The initial position of the arrow of pressure and vacuum gauge 6 (Fig. 2) should correspond to position “0”. If necessary, adjust the initial position of the arrow using the adjusting screw; to do this, remove the plug from the pressure-vacuum gauge glass and set the arrow position (“set to zero”) through the hole in the glass.

Start stopwatch 12 and check its functionality with a test run.

Move pump handle 7 to working position, turning the lock 8 in the direction of the arrow indicated on the panel.

Prepare the MGn head dummy for connection to the system according to the method outlined in the operating manual for the dummy.

  • Checking the tightness of the system with a connected head dummy (or test disk) is carried out sequentially with excess and vacuum pressure.

Install adapter No. 4 into coupling 1 (Fig. 2) and connect the head dummy (or test disk) to it. Install plug No. 6 on the headform (or plug the hole in the body of the test disk).

Move shift lever 5 to the “excess” (“vacuum”) position.

Using the pump handle 7, smoothly create excess (vacuum) pressure in the system

1000 Pa. Pressure control using pressure and vacuum gauge 6.

By pressing reset button 4, reduce the pressure in the system to 950 ± 50 Pa.

Turn on stopwatch 12. Maintain the system for 1 minute, observing the readings of the pressure and vacuum gauge.

A system with a headform (or test disk) connected is considered sealed if no change in pressure is observed.

Attention! To avoid freezing of the gauge needle, it is not recommended to create an excess pressure of more than 1250 Pa (vacuum pressure - less than minus 1250 Pa); to eliminate the freezing of the pointer, press and hold the reset button 4 until the pointer begins to move.

  • Working with the system.
  • When connecting to the breathing apparatus system, apply CIATIM-221 lubricant to the O-rings.
  • When installing the front part on the head dummy, wipe the seal of the front part and the dummy in the place where the seal fits with a swab, generously soaked in tap water, to remove abrasive materials and other foreign particles.

Checks should be carried out on the undried front part and the dummy or by applying a soap solution to them to increase the tightness of the obturation site.

  • Before installing the front part on the MGn head dummy, release the pressure in the dummy to marks 1…2 on the indicator scale by moving and holding the switch lever in position

"reset". Place the front part on the dummy. Raise the pressure in the dummy to the upper line of the green sector of the indicator scale, and after holding for 1.5 ± 0.5 minutes, release the pressure until the indicator needle reaches the middle of the green sector. This value pressure in the dummy is optimal for testing all types of facial parts.

  • To install the front part on the test disk, it is necessary to rotate the flywheel 17 (left-hand thread) (Fig. 1) to remove the pressure disk 18 from the front disk. Put the front part on disk 14, having first thrown the headband onto the front side. By rotating the flywheel, press the pressure disk against the front part, holding the front part belts.
  • Checking breathing apparatus.
  • Checking the vacuum air pressure at which the lung demand valve turns on.

Install directly or via adapter (No. 5 or No. 10) turned off lung demand valve into coupling 1 (Fig. 2) of the system.

Open the cylinder valve.

Pump handle 7 slowly create a vacuum pressure in the system and observe the readings of the pressure and vacuum gauge 6.

The moment when the pressure begins to increase is considered the moment the lung demand valve is turned on.

Close the cylinder valve.

Relieve the pressure in the system by pressing the reset button 4.

  • Checking the amount of excess air pressure created by the lung demand valve.

Install directly or through an adapter (No. 5 or No. 10) the lung demand valve into coupling 1 (Fig. 2) of the system.

Turn on the lung demand valve (how to turn on the lung demand valve - see the operating instructions for the breathing apparatus).

Open the cylinder valve.

Monitor the amount of excess pressure using a pressure and vacuum gauge 6.

Close the cylinder valve.

Relieve the pressure in the system by pressing the reset button 4.

Disconnect the lung demand valve from the system.

Attention! When checking the lung demand valve of the AP-98-7K device, before installing it on the system, it is necessary to open the cylinder valve, allow the lung demand valve to close (closing is characterized by a strong hiss of air for several seconds), close the cylinder valve and then install the lung demand valve on the system.

  • Checking the amount of excess pressure in the under-mask space of the front part at zero air flow and the tightness of the air duct system of the breathing apparatus.

Install the lung demand valve into the valve box socket of the front part. Turn on the lung demand valve.

Open the cylinder valve. Record the readings of the pressure and vacuum gauge 6.

Close the cylinder valve.

Turn on the stopwatch and observe the readings of the device’s pressure gauge for 1 minute.

Relieve the pressure in the system by pressing the reset button 4.

The air duct system of the device is considered sealed if within 1 minute the pressure drop does not exceed 2.0 MPa.

  • Checking the air pressure at which the exhalation valve of the front part opens.

Install adapter No. 4 into coupling 1 of the system and connect the head dummy (or test disk) to it. Check the system’s own tightness according to clause 2.1.2 of this manual.

Place the front part on the headform (or test disc).

Install turned off lung demand valve into the valve box socket of the front part. Move shift lever 5 to the “excess” position.

Pump handle 7 slowly create excess pressure in the system and observe the readings of the pressure and vacuum gauge 6.

The moment when the pressure in the system stops increasing is considered the moment the exhalation valve of the front part opens.

  • Checking the value of the reduced pressure, the opening pressure of the safety valve and the tightness of the reducer valve.

Connect the reduced pressure line of the device directly or through an adapter (No. 1, No. 2, No. 20, No. 30 or No. 40) to the quick-release coupling (QC) of the system.

Open the cylinder valve.

Start the stopwatch. Monitor the reduced pressure value using the system pressure gauge for 1 minute.

Check the opening pressure of the pressure reducer safety valve according to the procedure outlined in the operating manual for the breathing apparatus. Record the opening pressure of the safety valve using the system pressure gauge.

Close the cylinder valve.

Relieve the pressure in the system by pressing the reset button 9.

The reducer valve is considered sealed if the value of the reduced pressure does not change.

  • Checking the tightness of the front part under vacuum pressure.

Install adapter No. 4 into coupling 1 of the system and connect the head dummy (or test disk) to it. Check the system’s own tightness according to clause 2.1.2 of this manual.

Place the front part on the headform (or test disc). Install the plug

(pulmonary demand valve with a plugged hose) into the inhalation line of the front part.

Move shift lever 5 to the “vacuum” position.

Use pump handle 7 to create a vacuum pressure of 1100 ± 100 Pa in the system. Pressure control using pressure and vacuum gauge 6.

By pressing reset button 4, reduce the pressure in the system to 980 ± 20 Pa. Maintain the system for 1 minute, observing the pressure-vacuum gauge readings.

Relieve the pressure in the system by pressing the reset button 4.

Remove the plug from the inhalation line.

The front part is considered sealed if the pressure drop in it does not exceed 50 Pa per minute.

  • Checking the tightness of the rescue device under vacuum pressure.

Install adapter No. 4 into coupling 1 of the system and connect the head dummy (or test disk) to it. Check the system’s own tightness according to clause 2.1.2 of this manual.

Place the face of the rescue device onto the headform (or test disk). Attach the lung demand valve of the rescue device with the plugged hose to the front part.

Move shift lever 5 to the “vacuum” position.

Use pump handle 7 to create a vacuum pressure of 900 ± 20 Pa in the system. Pressure control using pressure and vacuum gauge 6.

Turn on stopwatch 12. Maintain the system for 2.5 ± 0.5 minutes.

By pressing reset button 4, reduce the pressure in the system to 800 ± 20 Pa. Maintain the system for 1 minute, observing the pressure-vacuum gauge readings.

Relieve the pressure in the system by pressing the reset button 4.

Remove the plug from the lung demand valve.

The rescue device is considered sealed if the pressure drop in 1 minute does not exceed 100 Pa.

When used in the ShMP-1 rescue device, a pressure drop of 353 Pa is allowed when creating a vacuum pressure of 1177 Pa. When checking, install plug No. 8 in the exhalation valve.

  • Checking the vacuum air pressure at which the lung demand valve of the rescue device opens without excess pressure under the front part.

The check is carried out according to the methodology outlined in paragraph 2.2.5.1 of this manual.

OPERATING INSTRUCTIONS

  • The system can be operated in stationary conditions at ambient temperatures from 5 to 50C and relative humidity from 30 to 80%.
  • Before commissioning, it is necessary to remove the transport seal, check by external inspection the condition of the system and compliance of the completeness with the list specified in the system passport.
  • After storing or transporting the system without packaging at a temperature below 0C, keep the system for 2 hours at a temperature from 5 to 50C.
  • Before each use of the system, it is necessary to check the tightness of the system with a connected headform (or test disk) in accordance with this manual.
  • To more quickly relieve pressure in the low-pressure unit, instead of reset button 4 (Fig. 2), you can use switch lever 5, moving it to any of the positions (“excess” or “vacuum”).

It is prohibited to create a pressure of more than 61250 Pa with the pump, or to connect a pressure source of more than 2.0 MPa to the quick-release connection.

  • Test the breathing apparatus at a constant ambient temperature. The permissible rate of temperature change is 61C per hour.
  • Protect the system from falls and impacts.

After completing work with the system, you must:

  • set the pump handle 7 to the transport position;
  • install plug 3 on coupling 1;
  • install the cap on the quick connector

The pressure-vacuum gauge and pressure gauge used in the system must be checked at least once a year in accordance with the established procedure.

The frequency of subsequent re-examination of devices is established by the consumer in agreement with the territorial body of the State Metrological Service.

MAINTENANCE

  • For operational issues, Maintenance, purchasing spare parts and repairing the system, please contact the manufacturer or its service centers.
  • Protect the system, especially the glass of the pressure gauge, pressure-vacuum gauge and stopwatch from damage.
  • Monitor the condition of the sealing elements included in the system and the adapter kit.
  • Conduct an external inspection of the system to detect damage. Clean the housing and panel from dust and dirt.

SECURITY MEASURES

Safety during operation of the system is ensured by compliance with the requirements.

“Manuals on the gas and smoke protection service of the State Fire Service of the Ministry of Internal Affairs of Russia” and “Rules for the design and safe operation vessels operating under pressure" (PB 03-576-03).

TRANSPORTATION AND STORAGE

  • The system can be transported by all types of transport in closed and dry vehicles at temperatures from minus 60 to 50C and relative humidity up to 100%.
  • If transportation is carried out in open vehicles, then the container with the systems must be protected from exposure to precipitation, and when transported by sea, be in the hold of the ship.

Transportation and storage together with gasoline, kerosene, oils, alkalis and other substances that are harmful to metal, rubber and plastic are not allowed.

  • During transportation, as well as during unloading or loading, all precautions must be taken in accordance with the markings on the packaging container.
  • During storage, the system must be protected from direct contact sun rays and be at a distance of at least 1 m from heating devices. Relative humidity should not exceed 80% at a temperature of 25C, air temperature should be in the range from 5 to 40C.

POSSIBLE MALFUNCTIONS AND METHODS OF THEIR ELIMINATION

Possible malfunction Most likely cause of the problem Troubleshooting methods
System leakage Damage to sealing gasket 2 (Fig. 2). Inspect the sealing gasket; if damage is found, replace the gasket.
Leaks at the joints of the pneumatic elements of the system. Wash the joints. Apply pressure. Visually determine the location of the leak. Tighten the connection. Replace if necessary.
Damage to tubes. Inspect the tubes; if damaged tubes are found, replace them with new ones.
The pneumatic element of the system is leaking. Replace with new one.
Adapters leaking Damage to the sealing element of the adapter. Inspect the sealing element. Replace if damaged.


Control unit KU-9V

The KU-9V control unit is designed to control the main operational parameters breathing apparatus with compressed air for compliance with the requirements set out in the operating manuals for breathing apparatus and the Order of the Ministry of Emergency Situations of Russia dated 01/09/2013 No. 3 “On approval of the Rules for carrying out emergency rescue operations by personnel of the Federal Fire Service of the State Fire Service when extinguishing fires using means personal protection respiratory and visual organs in an unsuitable for breathing environment", such as: AP-98-7K, AP-2000, AP "Sever", AP "Omega", AIR-98MI, ​​AIR-300SV, PTS+90D "BASIS", RA-90 Plus, Spiromatic QS, AIR-PAK 4.5 Fifty.

The main purpose of the KU-9V device is RPE check, namely breathing apparatus used in emergency situations (in particular in case of fire).

Using the installation, it is possible to create and measure excess and vacuum pressure (0-1000 Pa), as well as reduced pressure in the range from 0 to 1.5 MPa. KU-9V allows testing of various breathing devices certified in the territory Russian Federation(for example, AP Omega, AP 2000, etc.).

Checking 1 breathing apparatus

Check 1 breathing apparatus is done as follows:

1. The device is inspected for compliance with the configuration and the absence of visible defects. For this purpose, a number of operations are performed:

  • Disconnect the mask from the automatic breathing system.
  • Carefully inspect with inside chin cup.
  • Check the glass and body of the mask, and other elements of the mask (mask liner, breathing valves, intercom) for possible cracks and breaks.

After this, a general inspection of the product is carried out (reliability of fastening of the hanging device, oxygen cylinders, performance of the pressure gauge). At the same time, pay close attention to the presence mechanical damage elements of the device.

2. At the next stage, the respiratory function is checked automatic installation, the moment the exhalation valve is turned on and the excess pressure inside the mask. For this purpose, the following actions are performed:

  • Turn off the lung demand valve.
  • Set the oxygen tank valve to the “open” position.
  • Switch the lever (4) to “–” and smoothly operate the pump, while the moment the pulmonary apparatus begins to operate is the moment when the pressure begins to increase.
  • Switch lever (4) to “+”. At the same time, gradually increase the excess pressure, checking it with the device (9). The period when the pressure stops increasing is the moment the exhalation valve (10) is activated.

For a working device, the excess pressure should vary from 200 to 400 Pa, while the exhalation valve activation indicator should be slightly higher, but not more than 600 Pa.

3. At the third stage, data from high and reduced pressures is taken and the tightness of the device is checked:

  • The hose of the KU-9V device is connected to the device being tested.
  • The cylinder valve is set to the “open” position. In this case, the cylinder must be filled to operating pressure.
  • Data about high blood pressure(external pressure gauge of the breathing device) and reduced pressure readings (pressure gauge on KU-9V). The values ​​should be between 0.45 and 0.9 MPa.
  • The cylinder valve is turned to the “closed” position and the time of decrease in high and reduced pressure is measured with a stopwatch. In one minute, the pressure should not drop by more than 2 MPa (the device is sealed).

4. The functionality of the additional oxygen supply device and the pressure indicator at which the alarm is activated are checked:

The additional oxygen supply device is turned on by pressing the corresponding button. If you hear a characteristic sound produced by a stream of air before the signal turns on. The alarm system is considered operational if it is activated when the pressure decreases to 5.5 MPa.

5. On final stage The pressure in the cylinder is checked. When opening the tap, the pressure gauge should show a minimum of 24.5 MPa.

All readings received are recorded in a log book. RPE checks No1.

Article sent by: Brazil

1. We screw the plug to the coupling of the device and use the pump of the device to create an excess pressure of 1000 Pa. Turn on the stopwatch for 1 minute (no pressure drop should be observed).

(there should be no pressure drop).

Leak test of SCAD-1 with front part

1. We screw the hose from the head with the adapter to the coupling to the front part of the device. We create an excess pressure of 1000 Pa. Turn on the stopwatch for 1 minute (there should be no drop in pressure).

2. We create a vacuum pressure of 1000 Pa with the pump. Turn on the stopwatch for 1 minute

(there should be no drop in pressure).1 minute (there should be no drop in pressure).

1. External inspection of the panoramic mask.

Check the completeness, integrity of the front part, glass and half-clips, condition of the headband straps and valve box.

2. External inspection of the device

Make sure there is no mechanical damage to the suspension system, pressure gauge and other elements. Check the reliability of the connection between the mask and the lung demand valve.

3. Checking the operation of the lung demand valve, the exhalation valve and the pressure in the submask space.

Place the mask on the headform and connect the outlet to the SCAD. Having turned off the lung demand valve, open the cylinder valve and use the SCADA pump to create a vacuum until the lung demand valve is activated. Monitor the readings of the SCAD mono-vacuum meter. The pulmonary valve and exhalation valve are considered to be in good working order if the pressure in the submask space is 300-450 Pa and there is no air leakage.

4.Checking the tightness of the high pressure system.

After closing the cylinder valve, monitor the pressure gauge reading; the pressure drop should not exceed 2 MPa.

Sequence of checks No. 1, No. 2 of breathing apparatus

1. External inspection:

Check the completeness of the panoramic mask, the integrity of the front part, glass and half-clips, the condition of the headband straps and the valve box.


Make sure there is no mechanical damage to the suspension system, pressure gauge and other elements.

Check the reliability of the connection between the mask and the lung demand valve.

2.

Checking the activation value of the lung demand valve:


Attach an adapter to coupling 13 (supplied with the unit). Connect the lung demand valve of the device being tested to coupling 13. Open the cylinder valve.

Pump handle 8 slowly create vacuum pressure in the control and measuring unit by moving the lever of the pneumatic distributor5 to the “vacuum” position and observe the readings of the vacuum pressure gauge6. The moment when the pressure begins to increase is considered the moment the lung demand valve is turned on.

Close the cylinder valve.

Disconnect the lung demand valve from the installation.

The vacuum pressure of the valve opening without excess pressure under the front part should be from 50 to 350 Pa

A working check of the RPE is carried out:

  • Before using RPE in an unsuitable for breathing environment, an operational check is carried out in accordance with the requirements of the RPE manufacturer's operating manual.
  • When replacing a RPE cylinder at the site of fire extinguishing in an environment unsuitable for breathing (classes, training), a working check of the RPE is carried out.
  • A working check of the RPE is carried out by a gas and smoke protection specialist at the command of the GDZS flight commander (training leader): “Link, check your breathing apparatus”. The operating test time should not exceed 1 minute.

At the end of the working check, the gas and smoke protector reports to the GDZS flight commander (leader of the lesson) about readiness for switching on and the value of the working pressure in the cylinder (cylinders): “Gas and smoke protector Petrov is ready to turn on, pressure is 280 atmospheres”.

Permission to include a gas and smoke protection device in the RPE is given by the GDZS flight commander (training leader) after reporting to him about positive results operational check, serviceability and completeness: “Link, put on the breathing apparatus”.

Inclusion in RPE is carried out directly at the entrance to an environment unsuitable for breathing. The GDZS unit returns from an unsuitable for breathing environment only in full force. Switching off from RPE is carried out at fresh air at the command of the flight commander: “Link, switch off the breathing apparatus”.

Additional in the video

Procedure for carrying out a working inspection

Need to check:

  1. The serviceability of the mask and the correct connection of the lung demand valve to it.
  2. Vacuum tightness of the apparatus.
  3. Operation of the lung demand valve and mask exhalation valve.
  4. Triggering of the alarm device.
  5. Air pressure in the cylinder(s).

The serviceability of the mask and the correct connection of the lung demand valve to it are checked visually. Check the absence of damage to the mask elements and the reliability of the connection between the lung demand valve and the mask, and for type 2 additionally:

  • by rotating the lung demand valve 2 (Figures 6 and 7), make sure that the latch 2.1 is closed;
  • make sure that the bypass handwheel 2.4 is in the off position or turn it off by turning it 90° clockwise.

Checking the tightness of the apparatus for vacuum is carried out with the cylinder valve(s) closed. To check, you need to press the mask tightly to your face and try to take a shallow breath.

ATTENTION!!! ATTEMPTING TO TAKE A SHARP DEEP BREATH CAN LEAD TO LUNG BAROTRAUMA!

If, when inhaling, a large resistance is created that does not allow further inhalation and does not decrease within 2-3 s, the device is considered sealed.

For this:

  • turn off the lung demand valve mechanism, for which press button 2.2 all the way (Figures 5, 6 and 7), fix it for 1 - 2 s, then smoothly release it;
  • open the valve of the cylinder (one of the cylinders);
  • put on a mask and make adjustments;
  • after the first deep breath, make sure that the lung demand valve has turned on and excess pressure has arisen in the cavity of the mask, for which they take several breaths and exhalations;
  • then, holding their breath, they put their finger under the seal of the mask and make sure that there is a constant flow of air from under the mask;
  • remove your finger from under the seal and, holding your breath for about 5-10 seconds, listen to make sure there is no air leakage.

If a leak is detected, adjust the position of the mask by tightening the straps, avoiding overtightening, and recheck the absence of leaks. After this, close the valve, turn off the lung demand valve and remove the mask.

Checking the operation of the alarm device is carried out in the following sequence:

  • open and close the valve of the cylinder (one of the cylinders);
  • by carefully pressing the bypass button and holding it in this position (type 1) or smoothly turning the bypass handwheel (type 2), bleed air from the internal cavities of the device, while simultaneously observing the readings of the device’s pressure gauge;
  • at the moment the sound signal occurs, note the pressure gauge reading and make sure that it meets the requirements of the operating manual for the breathing apparatus.

The air pressure in the cylinder(s) is checked with the valve(s) open using a pressure gauge. When checking, record the pressure gauge reading, which must be at least 25.3 MPa (260 kgf/cm2).

When performing inspection No. 1 of the device, you must check:

Checking the air duct systems of the installation and the dummy for leaks at excess and vacuum pressure. The test is carried out sequentially: first at excess pressure, then at vacuum pressure.

To check it is necessary: ​​- seal hole A in the dummy with a plug;

Set the distributor handle to position - (+);

Create an excess or vacuum pressure with the pump, slightly exceeding 1000 Pa, controlled by a pressure-vacuum gauge;

Move the distributor handle to the CLOSED position;

Allow 1 minute to stabilize the pressure and set by briefly pressing the pressure release valve button (950) Pa;

Turn on the stopwatch and after 1 minute record the pressure-vacuum meter reading again. The air duct system of the installation is considered sealed if the pressure and vacuum gauge reading has not changed. After checking, remove the plug from hole A in the dummy.

1. Check the serviceability of the DASV testing device, according to the operating manual;

2. Serviceability of the front part;

(Check the serviceability of the front part visually. If front part is fully completed and there is no damage to its elements, it is considered to be in good working order).

3. Serviceability of the device as a whole;

(When checking the device as a whole, it is necessary to check the reliability of fastening of the suspension system, cylinder (cylinders) and pressure gauge, make sure that there are no mechanical damage to components and parts, as well as the reliability of the connection of the front part with the lung demand valve. Visual inspection of cylinders is carried out in accordance with the operating instructions and instructions for checking the cylinder, and in the absence of these guidelines according to the requirements).

4. Serviceability of the pulmonary valve and exhalation valve;

(Check the serviceability of the lung demand valve and exhalation valve in accordance with the operating instructions for the testing device)

5. Tightness of high and reduced pressure lines;

(Check the tightness of the high and reduced pressure lines in accordance with the operating instructions for the testing device).

6. Presence of excess pressure in the submask space;

(Check for the presence of excess pressure in the under-mask space of the front part in accordance with the operating instructions for the testing device).

7. The pressure value at which the alarm device is triggered;

(Check the pressure value at which the alarm device is activated as follows:

· close the valve(s) of the cylinder(s) with the filled air duct system of the apparatus;


· carefully, pressing the additional supply (bypass) button of the lung demand valve and holding it in this position, bleed air from the internal cavities of the device until the sound signal turns on, sound signal must operate at the air pressure in the cylinder(s) specified in the instruction manual.

8. Tightness of the air duct system with a connected rescue device (if any);

(Check on a device with an air pressure in the cylinder of 29.4 MPa and a connected rescue device. Apply a soap film to the junction of the fitting with the adapter connector and the joint. Open the cylinder valve. The device is considered sealed if no air bubbles are released within 1 minute or stretching of the soap film on the joints.)

9. Serviceability of the auxiliary air supply device of the lung demand valve;

(To check the serviceability of the additional air supply device, open the valve of the cylinder (cylinders) and, carefully, pressing the additional supply (bypass) button of the lung demand valve, turn on the additional supply. If a characteristic sound of air flow is heard, the device is considered to be in working order.)

10. Serviceability of the additional air supply device of the lung demand valve of the rescue device (if any);

(To check the serviceability of the additional supply device of the rescue device, open the valve of the cylinder (cylinders) and press the additional supply button. If a characteristic sound of air flow is heard, the device is considered to be in working order.)

(Check the serviceability of the gearbox with a test device in accordance with the operating instructions.)

12. Air pressure in the cylinder(s).

(Check the air pressure in the cylinder(s) according to the pressure gauge reading by opening and closing the valve of the cylinder(s) with the lung demand valve turned off).

13. The results of the inspection are recorded in the inspection log No. 1.

Final part

The teacher issues an assignment for practical lesson, answers questions that students have. Checks notes randomly.

VI. Literature

a) Basic literature:

1. Organization, management and equipment of gas and smoke protection service: Textbook. allowance/Averyanov V.T. [and etc.]. / ed. V.S. Artamonova. - St. Petersburg: Publishing house of St. Petersburg State Fire Service EMERCOM of Russia, 2011. - 272 p.

1. Gas and smoke protection service in questions and answers: Organization, management and equipment of the gas and smoke protection service: Textbook. allowance/Averyanov V.T. [and etc.]. / ed. V.S. Artamonova. - St. Petersburg: Publishing house of St. Petersburg State Fire Service EMERCOM of Russia, 2011. - 252 p.

c) Regulatory legal acts:

2. Order of the Ministry of Emergency Situations of Russia dated January 09, 2013 No. 3 “On approval of the rules for carrying out emergency rescue operations by personnel of the federal fire service of the State Fire Service when extinguishing fires using personal protective equipment for the respiratory and visual organs in an unsuitable environment for breathing.”

3. Order No. 300 of 04/08/2014 “On the organization of the activities of the gas and smoke protection service in the divisions of the Federal Border Guard Service in the Primorsky Territory”

4. “The procedure for extinguishing fires by units fire department" Approved by Order of the Ministry of Emergency Situations of Russia No. 156 dated March 31, 2011.

5. Order No. 630 dated December 31, 2002 No. 630. On the approval and implementation of labor protection rules in the units of the state fire service of the Ministry of Emergency Situations of Russia (POTRO-01-2002).

6. the federal law No. 69-FZ “On fire safety» from 12/21/1994

7. Order of the GUGPS Ministry of Internal Affairs of Russia No. 86 dated 09.11.99. “Regulations on the procedure for certification of gas and smoke protectors in governing bodies, divisions of the State Fire Service of the Ministry of Internal Affairs of Russia and fire-technical educational institutions The Ministry of Internal Affairs of Russia has the right to conduct combat operations to extinguish fires in an unsuitable for breathing environment.”